Hi folks,
I have a 2016 Westerbeke 10kW BTDA diesel generator on our boat that failed to start last weekend. It has less than a 100 hours on it and we are the single owners. Up until now it has never had starting issues. I started the troubleshooting process consulting Nigel Calder's diesel mechanic book but, looking for some additional help. I am looking at this as a good opportunity to work on my troubleshooting skills.
The engine looks like it attempts to crank over but, then stops. This engine needs to have the pre-heat button held down priori to starting for the glow plugs. When I hold down the pre-heat you can hear the fuel lift pump clicking which I believe is normal. I have upload a 10 sec video of the attempted startup ( https://youtu.be/eS7MrMLN5DM ).
Last time this generator ran was last week of Dec. Ran for about 1-2 hours with heat pumps and space heater running while we took it out for a cruise. We usually run the generator at least every 3 months and like to run for an hour and load up the generator.
So here is what I have worked through so far.
1. Battery charge level. 5 yr old AGM but, voltage look good and no reason to suspect the battery had failed. Disconnected battery and attempted to start of 8Dx2 AGM used for Inverter bank. Same result.
2. Cable run from battery -> battery-swtch -> generator is less then 12' and direct run to frame of gen (-) and starter (+). I cleaned up connectors on both ends (no rust) and confirmed low resistance < 0.1 ohm.
3. Ruled out waterlock. Thru hull is always closed when generator is not running and exhaust outlet is above waterline with a riser.
4. Checked fuel manifold is open and Racor filter a-ok after visual inspection. Less then 30 hours on it and I changed the fuel filter last in 2019.
5. Hooked up AMP meter to battery cable during start and say at most 180A being briefly pulled.
6. Hooked up AMP meter onto the pre-heat solenoid on the output wire (VIO/RED) and would see 50A draw when pre-heat switch is engaged. Seems high as the manual says 8-9A per glow plug x 3 = 24-27A
7. I have not tested the glow plugs yet but, I ran them for 25 seconds with the pre-heat and they did not feel hot to the touch or warm per some recommendations.
8. I did a voltage test from the battery (-) to the control wire "B" to the pre-heat solenoid and saw 10.6V when pre-heat switch engaged. I assume that is expected with voltage drop on the battery with draw from the glow plugs.
9. I made an assumption that the starter + starter solenoid is working as I can see the AC generator spin when the engine attempts to crank in the video. Maybe that is a bad assumption.
10. So per this forum post (link below) there are a number of items in the starter circuit that can cause issues. I have identified them all on the engine but, not clear what is a good/bad reading on them. I took some readings of the water temp switch, oil pressure switch, and aux oil pressure switch.
11. Printed out wiring diagram and started identifying components on generator.
Good news is I don't need the generator ASAP so I can spend time learning how the components work and diagnose if they are working correctly.
Related forum post.
https://www.trawlerforum.com/forums/s6/westerbeke-5kw-genset-diagnostic-question-46754.html
I have a 2016 Westerbeke 10kW BTDA diesel generator on our boat that failed to start last weekend. It has less than a 100 hours on it and we are the single owners. Up until now it has never had starting issues. I started the troubleshooting process consulting Nigel Calder's diesel mechanic book but, looking for some additional help. I am looking at this as a good opportunity to work on my troubleshooting skills.
The engine looks like it attempts to crank over but, then stops. This engine needs to have the pre-heat button held down priori to starting for the glow plugs. When I hold down the pre-heat you can hear the fuel lift pump clicking which I believe is normal. I have upload a 10 sec video of the attempted startup ( https://youtu.be/eS7MrMLN5DM ).
Last time this generator ran was last week of Dec. Ran for about 1-2 hours with heat pumps and space heater running while we took it out for a cruise. We usually run the generator at least every 3 months and like to run for an hour and load up the generator.
So here is what I have worked through so far.
1. Battery charge level. 5 yr old AGM but, voltage look good and no reason to suspect the battery had failed. Disconnected battery and attempted to start of 8Dx2 AGM used for Inverter bank. Same result.
2. Cable run from battery -> battery-swtch -> generator is less then 12' and direct run to frame of gen (-) and starter (+). I cleaned up connectors on both ends (no rust) and confirmed low resistance < 0.1 ohm.
3. Ruled out waterlock. Thru hull is always closed when generator is not running and exhaust outlet is above waterline with a riser.
4. Checked fuel manifold is open and Racor filter a-ok after visual inspection. Less then 30 hours on it and I changed the fuel filter last in 2019.
5. Hooked up AMP meter to battery cable during start and say at most 180A being briefly pulled.
6. Hooked up AMP meter onto the pre-heat solenoid on the output wire (VIO/RED) and would see 50A draw when pre-heat switch is engaged. Seems high as the manual says 8-9A per glow plug x 3 = 24-27A
7. I have not tested the glow plugs yet but, I ran them for 25 seconds with the pre-heat and they did not feel hot to the touch or warm per some recommendations.
8. I did a voltage test from the battery (-) to the control wire "B" to the pre-heat solenoid and saw 10.6V when pre-heat switch engaged. I assume that is expected with voltage drop on the battery with draw from the glow plugs.
9. I made an assumption that the starter + starter solenoid is working as I can see the AC generator spin when the engine attempts to crank in the video. Maybe that is a bad assumption.
10. So per this forum post (link below) there are a number of items in the starter circuit that can cause issues. I have identified them all on the engine but, not clear what is a good/bad reading on them. I took some readings of the water temp switch, oil pressure switch, and aux oil pressure switch.
11. Printed out wiring diagram and started identifying components on generator.
Good news is I don't need the generator ASAP so I can spend time learning how the components work and diagnose if they are working correctly.
Related forum post.
https://www.trawlerforum.com/forums/s6/westerbeke-5kw-genset-diagnostic-question-46754.html