So I went down to Queen City Yacht Club this morning for an electrical check that is required for being on their (eternal) moorage wait list. The club has new GFCI podiums with 30 amp power outlets. I have a Marinco 30>50 amp reverse splitter that came with the boat when we bought it last December and which has worked at several marinas we have visited that lack 50 amp power, even though I have worried that there might be something wrong with it because the LED at the output connector doesn’t light up. The inspector hooks it up to the podium, connects it to my shore power cable, turns on the podium breakers, and they immediately flip. We disconnect my shore power cable, flip the breakers back on, and test the splitter legs for power. There is current on each of the 30 amp legs, but no power on the 50 amp leg downstream of the junction. We drive over to Fisheries and I buy a new reverse splitter. We plug it in to the podium, turn on the breakers, and the light goes on. We test and have power now to the 50 amp connector. Turn off the breakers, connect my shore power cable, flip the breakers back on, and they trip again. Try a different podium, same result. So you’d think I have a ground fault. Except we have an isolation transformer, and we have connected the shore power cable directly to ELCI/GFCI protected 50 amp service without problems. Any thoughts why we would experience this problem only with the reverse Y splitter???