For sure, but how does it get out if a low rated fuse, or in our case, 200amp mrbf to 500amp ANL to 500amp breaker blows?
I certainly don't want something bad going on and having a monster high amperage fuse there allowing the bad to escalate.
To me that seems a bit like putting a bolt in a fuse holder
I'm no expert here but have been reading & trying to understand AIC / AIR.
The important point I have gathered is that very high amp flows... as in short circuits not just a high A use system.... cause many fuses to weld themselves together rather than simply open due to overload.
The larger the size of a batty bank the higher the AIC / AIR needs to be regardless of the fuse rating for a simple overload. They are two different and somewhat unrelated conditions.
I dont know if I'm correct but I think of the fuse as analogous to a switch...
Under " normal" conditions ( within the rated A capacity of the Sw) you can open the Sw and the circuit is protected. If the current flow is higher than the rating for the Sw there is a risk the Hi Amps will arc and weld the contacts together instead of openning the circuit.
The risk protected by the AIC rating of a fuse has nothing to do with simple overload protection rating and everything to do with dead short conditions (when normal overload protection of the wrong fuse type is no longer effective and fails as a shorted fuse vs an open circuit)
My understanding us a 100 A NRBF fuse will fail/open under a load of say 150A but if a batty bank is shorted and 20,000 A present the fuse may weld shut instead of opening and protecting the circuit. Likely a rare occurrence but that's my understanding of the whole topic / area if ABYC dealing with AIC. A type T fuse will still open and protect in the extreme cases where even NRBF exceed their ratings.
BTW I do not disagree with your use of MRBFs at each batty vs trying to protect a combined multi parallel bank. In fact, im thinking of using a similar approach w 4 GP3as in parallel. In that case V as long as each batty short circuit current is below thev10,000A AIR of the MRBFs they b should be protected.