My house bank of 4 8d AGMs will charge up to 100% SOC on a Balmar Smart Gauge and when charge is removed will stay at or above 13 volts for several hours with a 10 amp draw. After about 10-11 hours with a comparable draw it will be down to 92% with a voltage under load of 12.5 volts. The math says that is about right for 1000A house bank. However in the next 2 hours it will plummet to 60% SOC with the same load and voltage drop below 12 to around 11.6 and by then I start the main or generator.
Any ideas? I have isolated loads to see if some device has gone south and don't see any. I am suspecting a battery is acting up and plan to isolate each side to see if I can see which one it is. This morning I isolated all batteries and measured 12.4 volts on the starboard bank of 2 and 12.5 volts on the port bank. Plan is today to charge both banks to 100% and then run on only one bank to see what happens.
Tom
Any ideas? I have isolated loads to see if some device has gone south and don't see any. I am suspecting a battery is acting up and plan to isolate each side to see if I can see which one it is. This morning I isolated all batteries and measured 12.4 volts on the starboard bank of 2 and 12.5 volts on the port bank. Plan is today to charge both banks to 100% and then run on only one bank to see what happens.