2) Because you are using isolation transformers, you can simply tie all the neutrals together on the boat, and bond to ground at a single central point, typically at the load panel. This can often be a lot easier than trying to ensure only one bonding point is active at any given time.
All of twistedtree's advice aligns with my understanding and is very good, keeping in mind I'm an amateur and have only installed an isolation transformer once and very carefully studied E-11 at the time to do so.
I second the suggestion that a central bonding point probably makes this a lot easier to implement and understand both now and for any future modifications, but that won't work if your inverter can't disable its bonding. I don't think it can.
The other thing about your inverter is that it supports separate inputs for charger and transfer/passthrough. You don't have to use them.
NOTE: Freedom 25 Only. There are two options for configuring the AC input to the Freedom 25.
Dual Inputs: You may feed the internal battery charger separately from the transfer input which feeds the AC loads. In this case, connect one 30 Amp feed to the charger pigtails and another 30 Amp feed to the transfer switch input.
The advantage is to balance the AC loads when 2 legs of incoming AC power are available. These two feeds can be in or out of phase. Transfer will only occur when power is applied to both inputs. The charger can draw up to 27 Amps on one leg of power and the transfer switch can pass up to 30 Amps from the other leg of power.
Single Input: Feed both the battery charger and the transfer switch from the same AC input. In this case you will connect both pigtails together, Black to Black, White to White and Green to Green.
Side note. In reading E-11, it speaks on grounding on the metal case of the iso transformer. Because mine has a plastic housing, I wouldn’t need to ground there and my bonding would only be a jumper wire from my main ground bus to my main neutral bus?
Short answer, yes but
only if using option 2. Option 1 requires tying them at the transformer so that the neutral is disconnected when that input isn't active, thus severing the connection. Ground is still connected but neutral isn't.
Other answer: Your isolation transformers (which brand/model are they?) can never comply with the current E-11 to the letter so that makes understanding things slightly more complex. A lot of parts of electrical safety aren't purely black and white and change as technology and understanding progresses.
This is where what twistedtree said about the content of the draft E-11 applies, which is what would cover your situation if approved and what brings in the RCD, so you won't be able to exactly mirror the published E-11. So you can no longer blindly follow advice in Steve's article or others.
To state that in different words, I'd probably be fine using your isolation transformers but would absolutely put a RCD before them. I haven't researched that scenario in depth though.
There is long running debate / accusations around just what is and isn't safe for isolation transformers and if standards are rigged to support certain manufacturer's products.
Peter:
We did this on our vessel even with no isolation transformer. Doing this cured our trips on the newer GFIC shore pedestals.
That seems odd and wrong at first glance if I'm understanding, without an isolation transformer the "source" of power electrically speaking is not on the boat and thus neutral and ground shouldn't be connected when on shore power. They are only connected when using a "source" that is on the boat, such as an inverter or generator. This is one of the reasons why two pole breakers / transfer switches are necessary.
Marcs:
Did you consider one 50 amp/240V vs the two 30 amp /110V shore power inlets?
I'm not the original poster, so not sure this is directed at me but ...
I absolutely would pick one 50 amp 240v over two 30 amp 110v any day for my uses. Gives you almost twice the total power and much more robust physical plugs and safety margins. But it really depends on what shore power connections are available where you boat. But that brings a whole other set of considerations into play and is a more involved project.
So if neutral and ground never get connected, why is it the Gen and Inverter connect them when running? What’s the difference? All 3 are AC power sources
The power source for shore power, without isolation transformers, is considered to be shoreside. That is where the neutral ground connection is made.
With an isolation transformer, the transformer is now the "source" of the power.
Corrections welcome if I've misstated anything in my attempts to clarify.