GFCI + Pigtail = Mystery

The friendliest place on the web for anyone who enjoys boating.
If you have answers, please help by responding to the unanswered posts.
I believe the statement that the reverse Y will "never" work is not quite true. I carry one 50' 30 amp cord along with a smart reverse Y and have been able to get both legs to work using 2 different pedestals. I assume this is because it's using different neutrals. I have also come across a few marinas that understand the problem and have each pedestal wired with different legs on each side so the smart Y will work here also. I realize this is a bit cumbersome and not always possible but it has allowed us to run the AC in marinas with gfci and 30 amp only.

I'm no electrician so I'm not really sure how the magic works but it does.
It will work with out of phase 30A in an old marina but not with newer marina meeting current codes... big difference.
How could the Y adjust /;split the amps returning on the single ( 50A 125/250V) leg to the 2 30A 125V legs and match exactly the amps delivered from that recepticle? Possibly if everything is off and there is zero amps being drawn??? but once a load is applied the 125V hot and neutral will be unbalanced.
I have no interest in continuing any disagreement only trying to assist the OP answer his question. Only / best? Way it to find a friend / acquaintance with a 50A 125/250V pedestal and connect directly from pedestal to boat with a 50A cord while he is out of his slip... or haveva marina allow you to try connecting with a 50A cord.
 
Notes: 1) The reverse Y can never work if there is working ground fault sensing present on either of the 30A circuits. Technically, they are called EPD (equipment protection devices). It trips if the imbalance is more than 30ma. GFIs trip at around 5ma but the idea is the same. The reverse Y will work fine is one Y leg is on L1 and the other is L2 and both are without GF sensing.

2) The OP stated he had a 240V isolation transformer. They don't normally have a center tap connected to neutral on the primary side. If neutral comes aboard, it is usually not connected. Even if it was was, the current would all be flowing between L1 and L2 and not be returning to the one neutral and back out the other to balance the currents within 30 ma.

Think of the EPD breaker as a clamp on ammeter. For 30A, it clamps around hot and neutral and not ground. The resulting current fliwing in and out must be within 30 ma of canceling out to 0. For 50A, the clamp is around L1, L2 and neutral. If the current is flowing from L1 to L2, it cancels to 0 as in the 240V isolation transfomer or 240V load case. If is flows from L1 to N or L2 to N (or any combination), it again cancels to 0.

Consider two 30A EPD breakers with the isolation transformer or even a 240V load. Current flow from one EPD breaker but returns to the other one. Both are unbalanced and one if not both will trip. (It's a race.)
 
I believe the statement that the reverse Y will "never" work is not quite true. I carry one 50' 30 amp cord along with a smart reverse Y and have been able to get both legs to work using 2 different pedestals. I assume this is because it's using different neutrals. I have also come across a few marinas that understand the problem and have each pedestal wired with different legs on each side so the smart Y will work here also. I realize this is a bit cumbersome and not always possible but it has allowed us to run the AC in marinas with gfci and 30 amp only.


That may be bypassing the part about trying a Reverse Y with new GFCI pedestals (the "never work" part)? Did those places have the new GFCI pedestals?

-Chris
 
Clarification: I am are not talking about convenience outlets with the GFI buttons, I am referring to new "to code" EPD 30A outlets.
 
I think the only way to confirm whether your boat has any issues is to connect to a 50A 125/250V GFCI Pedestal and see if it trips. You will never be able to do this with the reverse Y.

Basically... in layman's terms... GFCI measures and ensures there is no imbalance in amps in the system (leakage out of the system).
With 30A 125V that means amps in via the hot matches (within milliamps) the amps returning via the neutral.
With 50A 125/250V system you have 3 wires... hot line 1, hot line 2 and a neutral and the neutral only carries the amps that are out of balance on L 1 + L 2.

The reverse Y will be useless in recently rebuilt marinas that meet current (no pun intended) codes.
I just got through to Marinco technical support and they have confirmed that this is the correct answer. You cannot use a reverse Y adapter with GFCI/ELCI protected podium because of the mismatch on the neutral line, full stop. Thanks everyone, this mystery is solved.
 
I just got through to Marinco technical support and they have confirmed that this is the correct answer. You cannot use a reverse Y adapter with GFCI/ELCI protected podium because of the mismatch on the neutral line, full stop. Thanks everyone, this mystery is solved.
Ask Miguel if you can do the test on a 50A pylon over by the recip dock instead.
 
@Sababa
You said you have a 30A single 125 to 50A dual 125 adapter.
In theory the 2 hots merge into one, one neutral, one ground. If that does not work I would like to know why not. The only other is the isolation transformer that could prevent it from working.
Of course 30A is less than you want.
 
I just got through to Marinco technical support and they have confirmed that this is the correct answer. You cannot use a reverse Y adapter with GFCI/ELCI protected podium because of the mismatch on the neutral line, full stop. Thanks everyone, this mystery is solved.
Ian
Thanks for reporting Marinco confirmation. I have never checked w them but have done some digging about GFCI ELCI after our home port marina was upgraded and many transient boaters ran into problems.
 
@Sababa
You said you have a 30A single 125 to 50A dual 125 adapter.
In theory the 2 hots merge into one, one neutral, one ground. If that does not work I would like to know why not. The only other is the isolation transformer that could prevent it from working.
Of course 30A is less than you want.
I don't know why the 30A single doesn't work. I'm assuming it has something to do with the isolation transformer but would appreciate any insight.
 
A Thought. Can you do a continuity test on the adapter to eliminate a internal wiring issue. As in ground to ground and nothing else, neutral to neutral then hot split to two 50A hot.
 
Ask Miguel if you can do the test on a 50A pylon over by the recip dock instead.
Notwithstanding what Marinco says, Miguel insists that he has had other club members successfully use the reverse Y adapters with the GFCI podiums and the hitch must be with my isolation transformer. He seems to be a bit prickly about it so I'm not going to push it. I don't know what to think at this point so I'm just going to figure out where I can line up 50 amp service with an inspector and take it from there.
 
I second the previous comments of you can not share a neutral between two seperate gfci circuits. This would lead one to say you cannot use splitters with Gfcis.
 
Notwithstanding what Marinco says, Miguel insists that he has had other club members successfully use the reverse Y adapters with the GFCI podiums and the hitch must be with my isolation transformer. He seems to be a bit prickly about it so I'm not going to push it. I don't know what to think at this point so I'm just going to figure out where I can line up 50 amp service with an inspector and take it from there.
My guess is his comment that's others have used reverse Y w updated ELCI us blowing smoke. He may not understand exactly what others situation or equipment was but Marinco knows and I would truct their reply.
 
I believe the statement that the reverse Y will "never" work is not quite true. I carry one 50' 30 amp cord along with a smart reverse Y and have been able to get both legs to work using 2 different pedestals. I assume this is because it's using different neutrals. I have also come across a few marinas that understand the problem and have each pedestal wired with different legs on each side so the smart Y will work here also. I realize this is a bit cumbersome and not always possible but it has allowed us to run the AC in marinas with gfci and 30 amp only.

I'm no electrician so I'm not really sure how the magic works but it does.
I think the 30A outlets you are plugged into are not GFCI outlets.
 
So an off the wall comment. Use a single 30a 125v to 50a 125/250v adapter. It won’t fire up your IT but it won’t trip the pedestal. There, you pasted the test, pedestal didn’t trip. Not his buisness if IT can’t work off a single 30a. Just make sure you get Assigned to a 50a slip.
 
I’ve spoken to the Commodore and they are going to let me do the test off the 50 amp connection either at my own slip or at the outstation depending on when and where I can get an inspector lined up. They are all volunteers and don’t charge anything so I can’t get too fussy.
 
I don't know why the 30A single doesn't work. I'm assuming it has something to do with the isolation transformer but would appreciate any insight.

Don't know the technicals, but for years owners in our club have confirmed there's no (sane) way to get a single 30A/125V shorepower supply through a 50A/250V isolation transformer.

Most of the those discussions evolved as owners grew into larger boats over the years (with 220V appliances) and as that maker began fitting isolation transformers as a matter of course, starting in circa 2003-ish. Often , this questions were about how to charge batteries while on the hard in winter, with only temporary storage lot power.

-Chris
 
Don't know the technicals, but for years owners in our club have confirmed there's no (sane) way to get a single 30A/125V shorepower supply through a 50A/250V isolation transformer.

Most of the those discussions evolved as owners grew into larger boats over the years (with 220V appliances) and as that maker began fitting isolation transformers as a matter of course, starting in circa 2003-ish. Often , this questions were about how to charge batteries while on the hard in winter, with only temporary storage lot power.

-Chris
If there's space on board, the way to do it (and I've seen something like this done from the factory on a Tiara) is a selector switch and a separate 120 -> 240V step-up transformer. So you have a single 30A inlet and a 50A inlet on the boat and select which one you're using (rather than using the 50A cord with an adapter). That assumes that the isolation transformer is intended to take straight 240V and make 120/240V split phase from it.
 

Latest posts

Back
Top Bottom