Ah, sorry for the confusion I see what you're saying. I don't have an adapter as there are so many different sockets I always just open the j-box (with the cord plugged in) and test at the breaker.
This has always seemed the simplest and most accurate way of checking for leakage. Any decent voltmeter measures milliamps, correct?With your shore power disconnected, and your inverters, and generators output isolated, use an ohm meter between your AC neutral and ground.
You should see an infinite reading.
If you do not you need to find and resolve the issue.
This has always seemed the simplest and most accurate way of checking for leakage. Any decent voltmeter measures milliamps, correct?
KS, when you say that the inverters and gensets are "isolated" please clarify precisely what you mean... thanks!!
If you had a hot wire rubbed through the insulation that contacted any of the bonded or DC grounded systems and it was going to ground...would that show up on the Neutral to Ground test???
cut for space.....
If you had a hot to ground short, it would most likely operate the circuit breaker or start a fire. To test for a hot to ground, you could also take an ohm meter reading. Hot to ground should be open. Hot to neutral will of course show your loads. I've honestly never seen a hot to ground short in a properly grounded system that did not operate the circuit breaker.
Much appreciated.What you are checking for is a neutral to ground short. This would create two parallel paths for what should be neutral current. One path is as it should be, from your loads to the boats panel, then out to shore power, over the neutral conductor. The other path, the one you do not want is from your loads, through ground, and sea water, back to shore power. (your shore power feed from the dock has its neutral shorted to ground and the ground conductor connected to earth ground)
Using the ohm meter is a very quick easy way to check for this. On the AC panel with no power to it you should see infinite resistance between ground and neutral.
You need to isolate the generator and inverter to do this. Thats because at the generator its neutral is connected to its frame, which is grounded. This is the only way, when running on generator power your ground actually does any good. Thats why your generator selector switch needs to disconnect both the hot and the neutral from the generator.
Your inverter/charger works kinda the same way. When AC is present at its input the neutral to ground is not shorted by the inverter. When the inverter is in invert mode (no AC present at its input), it automatically shorts neutral to ground, so that your ground actually is effective.
This all makes sense if we remember the job of the ground conductor. Its whole function is safety. The metal parts of your applicances are connected to the ground conductor. If there is a short in your appliance from hot to any metal part, the ground conductor provides a path for the current so we do not get electrocuted when we touch it.
If you had a hot to ground short, it would most likely operate the circuit breaker or start a fire. To test for a hot to ground, you could also take an ohm meter reading. Hot to ground should be open. Hot to neutral will of course show your loads. I've honestly never seen a hot to ground short in a properly grounded system that did not operate the circuit breaker.
Let me give it a try:
AC current from the shore power outlet goes down the black wire (I am using DC terms but bear with me) to the various appliances on the boat and then back up on the white (neutral wire). If you have any kind of fault- a short to ground in an appliance or wire then the current comes back on the green- the ground wire.
If you put an AC clamp on ammeter around all three wires you should see zero amps. The incoming black cancels out the outgoing white (or green).
But if you have a leak to the water (typically in the bilge) then some of the current will leave the boat through the water and there will be less current in the white or green wire and your clamp on ammeter will show some current.
It is a crude but effective test for AC leaks to the bilge.
But having said all of the above, AC leaks to the bilge don't cause what you are seeing. And I am not sure it is an electrolysis issue at all.
David