Melt Down Anybody??

The friendliest place on the web for anyone who enjoys boating.
If you have answers, please help by responding to the unanswered posts.

Edelweiss

Guru
Joined
May 15, 2011
Messages
1,860
Location
USA
Vessel Make
1976 Californian Tricabin LRC
Can anybody identify this mess??


Yes. . . It's a Smart Plug and it came off the boat near me!!

We have had two boat in our area, while at their respective docks melt down their Smart Plug shore power plugs. One was owner installed and the other by a licensed electrician. The company is blaming cold weather and on board heaters??

ps: I was looking at their website and I see they have an ETL approval, but not UL for the SmartPlug system??

Anybody have similar problems??
 

Attachments

  • Smart Plug.jpg
    Smart Plug.jpg
    46.8 KB · Views: 309
Last edited:
Can anybody identify this mess??
Yes. . . It's a Smart Plug and it came off the boat ??

Maybe the Marina has a problem. If there is an overload on the boat the 30 amp breaker on the dock should kick out. Or how about low voltage?
 
I was trying to figure out why my microwave wouldn't heat a cup of coffee and is I stuck my meter in the sockets - 88.5 volts! I started unplugging things and got the voltage back to 110 but it's straight Ohms Law, I figured I was drawing 40 amps off a 30 amp system and the marina's breaker didn't pop. Still haven't talked to them about it.
 
Salt plus high humidity creates corrosion on shore cord connections. Corrosion leads to high resistance. High resistance plus high amperage (winter heaters) leads to heat at the connections.

This is one of the leading causes of boat fires. You are lucky it only burned up the connector.

A 50-odd foot sportfish caught fire at the dock here a few weeks ago. Shore cord connector. Fortunately, fire was put out before it was engulfed.

Are leads tinned? Looks like they used shore cord cable for interior cable, I don't think that is tinned. Non-tinned more prone to corrosion.
 
Salt plus high humidity creates corrosion on shore cord connections. Corrosion leads to high resistance. High resistance plus high amperage (winter heaters) leads to heat at the connections. This is one of the leading causes of boat fires. You are lucky it only burned up the connector. A 50-odd foot sportfish caught fire at the dock here a few weeks ago. Shore cord connector. Fortunately, fire was put out before it was engulfed. Are leads tinned? Looks like they used shore cord cable for interior cable, I don't think that is tinned. Non-tinned more prone to corrosion.
We just ran some shore cord cable (bought it at pacer on a spool) which was marine grade, and it was all copper not tinned.
 
30 amp connectors with poor locking rings. Water intrusion resulted in high resistance connection and eventual melt down, Pretty scary stuff when you discover it. This was on a friends sailboat.
Back when I was a bubble head EM I saw a 1200 amp shore power cable melt down on the hull, really scary!
 

Attachments

  • 30 amp connectors.jpg
    30 amp connectors.jpg
    107.7 KB · Views: 224
Can anybody identify this mess??


Yes. . . It's a Smart Plug and it came off the boat near me!!

We have had two boat in our area, while at their respective docks melt down their Smart Plug shore power plugs. One was owner installed and the other by a licensed electrician. The company is blaming cold weather and on board heaters??

ps: I was looking at their website and I see they have an ETL approval, but not UL for the SmartPlug system??

Anybody have similar problems??
Their website goes on and on about how their design prevents overheating. It also indicates that they have a built in trip thermostat that cuts off the power when the unit overheats. So, why didn't the 'trip thermostat' cut off the power when the unit overheated? Well, the simplest explanation is because it is the trip thermostat that melted down. Hardly unusual if a PC board of some type is involved since these are frequently not fused with the result that even a .1 amp short will cause the things to catch on fire. My son's house almost burnt down when his Bosch dishwasher PCB, like many others, caught on fire without tripping the breaker.

If the company seriously is offering on board heaters or rain as a reason for these melt downs, I would steer well away from their product, since that would appear to be transparent B.S.
 
Maybe the Marina has a problem. If there is an overload on the boat the 30 amp breaker on the dock should kick out. Or how about low voltage?

Note the attached piece of dock cordage does not show excess heating or melting beyond the plug housing (water proof housing has been removed). Whatever the cause it appears to be internal to the plug, probably caused by arcing. The boat is a 2 year old tug. I'll get a look at the boat side of the plug this weekend. Don't know if he was using electric heaters or not. I know he has a diesel furnace.

The failures occurred at two different marinas. Our docks and
the Ports electrical are all new. We'll test his breaker just for kicks though.
 
Last edited:
Sure glad I didn't jump on the Smart plug bandwagon ...guess "smart" is in the eye of the beholder.

I have had several plug meltdowns but in the end...vigilance and maintenance are the best deterrents to electrical issues.
 
Without even investigating further, the problem is overloading.

The boats are flat overloading the circuits.

What people do not understand is that circuit breakers are not designed to react well to long term overloading conditions. They react very well to sudden applications of high current but not so welll to marginal overloading.

OK, circuit breakers work on a principal of inverse time overcurrent. What that means is that the time it takes a breaker to trip is inversely proportional to the current detected. More current, faster the breaker trips. Less current, the slower it trips.


So, its plausable to pull more than 30 amps through a breaker and not have it trip at all, or not for a very long time. Pull larger current and the breaker will trip faster.
 
Without even investigating further, the problem is overloading.

The boats are flat overloading the circuits.

What people do not understand is that circuit breakers are not designed to react well to long term overloading conditions. They react very well to sudden applications of high current but not so welll to marginal overloading.

OK, circuit breakers work on a principal of inverse time overcurrent. What that means is that the time it takes a breaker to trip is inversely proportional to the current detected. More current, faster the breaker trips. Less current, the slower it trips.


So, its plausable to pull more than 30 amps through a breaker and not have it trip at all, or not for a very long time. Pull larger current and the breaker will trip faster.

It has been documented I think by the NTSB that regular marine type CBs are pretty suspect as well as many aviation ones...at least into the early 2000 era for allowing slow overheating of wires to the pint of starting fires. Household CBs actually fared quite well in doing their jobs over a variety of tasks.

A few years back I couldn't get a brand new 20A marine CB to trip by sticking a screwdriver into a cigarette lighter plug to the point where the screwdriver welded itself into the socket. Not sure what was going on there...second breaker tried would trip.
 
Without even investigating further, the problem is overloading.

The boats are flat overloading the circuits.

What people do not understand is that circuit breakers are not designed to react well to long term overloading conditions. They react very well to sudden applications of high current but not so welll to marginal overloading.

OK, circuit breakers work on a principal of inverse time overcurrent. What that means is that the time it takes a breaker to trip is inversely proportional to the current detected. More current, faster the breaker trips. Less current, the slower it trips.


So, its plausable to pull more than 30 amps through a breaker and not have it trip at all, or not for a very long time. Pull larger current and the breaker will trip faster.
Possible, but not likely. The CBs on a marine pedestal are generally standard issue and yes, they will trip faster the greater the amperage they are subjected to, but we are talking a difference in milliseconds. Once you get to the point of melting wires ABSENT A PCB that can melt and cause fires at fractional amperage you have more than sufficient current to trip the breaker. If this wasn't the case, housefires would be rather more common.

If the breaker in this situation tripped, it didn't trip until after the melt down, which means that something had to be able to melt down at less than the breaker amperage. That something is highly likely to be whatever circuitry is used by SmartPlug in making their "trip thermostat", not overloading which would have tripped the breaker unless it is defective - possible but extremely unlikely.

Even if a 30 amp breaker were defective and allowed, say 50 amps to pass through it, the fact that this plug would have melted at that amperage would mean it was grossly under designed and should be avoided on that basis. I doubt that is the issue here, and expect, as noted, that the circuitry involved in their cute 'trip thermostat' that is designed to avoid overheating will likely prove to be the culprit.
 
A corroded connection can burn up at an amperage well below the breaker trip setpoint. That's where a lot of the danger is.
 
No matter how smart the plug is, an accidental dip into seawater will hasten corrosion.
 
So, some folks do not really beleive me when I say that a breaker can be significantly overloaded and still not trip.

Please see the link below to a square d breaker curve for a molded case circuit breaker, which is pretty typical of what we see in marina peds.

http://static.schneider-electric.us/docs/Circuit%20Protection/Molded%20Case%20Circuit%20Breakers/0100-400%20A%20Frame%20FA-LA/FA-FC-FH/0600DB0105.pdf

Here's the data.

at 1.5X the rated current (45 amps), trip time is between 90 and 400 seconds.

At 2X the rated current (60 amps) trip time is between 30 and 100 seconds

At 3X the rated current (90 amps) trip time is between 10 and 35 seconds

You guys get the idea.

How many amps, over how much time will it take to burn up #10 wire, and the connectors?

Boats burn up every year because of overloaded circuits. Owners trust the circuit breakers instead of managing the loads properly themselves.

But Alas there is some protection that works better. What I showed you above was for a SQUARE D brand molded case circuit breaker. Again, this is an industry standard for shore power feeds.

You can upgrade the protection in YOUR boat. Its simple. Replace your stock breaker with one of the Blue Sea shore power breakers. Posted below is the link to the product data page.

http://www.bluesea.com/products/7220/A-Series_Black_Toggle_Circuit_Breaker_-_Single_Pole_30A

This is a "faster" breaker having a trip of...

30 amps trips in 2-500 seconds
60 amps trips in .5 to 20 seconds

This faster breaker is much better. You cannot change your shore power. You can change the breaker in your boat.

Remember, especially you liveaboards. Load managment is up to you. Its your life at risk. Do not push the envelope.
 
Last edited:
If leaving a boat connected to shore power for a long period, would it be feasible to use dielectric grease to reduce the potential for corrosion on the plug?

Tom
 
Just had a email chat with Terry at SmartPlug, he is aware of both failures and here is his reply:

"This failure is due to a poor installation. The electrician or boat owner did not follow the instructions. I have provided you with the photos below of the other boat in the Anacortes area that had a connector failure. You can have the best product but if it is installed incorrectly they will fail.

Notice how there are no compression/bit marks on the yellow exterior sheathing of the cord. These photos document that the installer did not read the instructions to properly install our connector. The cord restraint jaws are designed to grip the yellow sheathing of the cord to eliminate pulling and strain on the wires that are installed in the connector. After prolonged use the pulling strain on the wires caused them to come loose which results in the failure as pictured in these photos. Please see the illustration below that is included with the installation instructions."

All I know is when I installed mine it was tough doing up the screws as to the pressure being put on the yellow jacket. No affiliation with Smartplug, just a happy customer.
 

Attachments

  • image001.jpg
    image001.jpg
    46.4 KB · Views: 194
  • image005.jpg
    image005.jpg
    23.5 KB · Views: 176
  • image004.jpg
    image004.jpg
    46.3 KB · Views: 189
Last edited:
Maybe this is one of the advantages of our system, (in fact most of the rest of the world) where we have 220-240 volt supply. ie Higher voltage = lower amperage or current. My impression is we have much less of this kind of trouble over here in Oz, although corrosion can still be an issue. I pull my plug both ends and clean it regularly, and apply a corrosion inhibitor.
 
Sure glad I didn't jump on the Smart plug bandwagon ...guess "smart" is in the eye of the beholder.

I have had several plug meltdowns but in the end...vigilance and maintenance are the best deterrents to electrical issues.


Ditto here. Salt and other factors are the real problem, and I don't think a SmartPlug is immune to, or can vanquish any of that. I'm sticking with my NEMA std twistlocks, and inspecting them regularly. They have failed, and will fail again. The trick is inspection and catching it early.
 
Of course when a really sensitive breaker is installed ,,folks will be moaning that the air cond blows the breaker every time it cycles on.

Have no idea if it is useful , but I cycle the breaker in a power pole , before pluging in.
 
Sure glad I didn't jump on the Smart plug bandwagon ...guess "smart" is in the eye of the beholder.

I have had several plug meltdowns but in the end...vigilance and maintenance are the best deterrents to electrical issues.

Ditto here. Salt and other factors are the real problem, and I don't think a SmartPlug is immune to, or can vanquish any of that. I'm sticking with my NEMA std twistlocks, and inspecting them regularly. They have failed, and will fail again. The trick is inspection and catching it early.

Disagree completely. I believe that the Smartplug is a superior product to the NEMA plug in both design and construction.

An interesting read here.
 
Low voltage will do that - happened to us last year at a state marina. Everyone had air cons running, we were seeing less than 100 volts coming into our boat. Went out to dinner, left our air conditioner on. Came back to a fried inlet that looked just like the one above. CB on the dock never tripped. The Marinco inlet which melted does have a protective housing on the inside, which I assume is to keep the boat from starting on fire. All the melting and burning was totally contained within the housing.
 
Disagree completely. I believe that the Smartplug is a superior product to the NEMA plug in both design and construction.

An interesting read here.

I don't doubt that it is superior in design and construction but they have not eliminated the base problem and who knows what their failure rate is compared to the standard plugs?

My bandwagon comment is typical for any new design or technology...while I may think the direction is good..I may just not think the learning curve for that design/tech is something I want to pay for and live through till the evidence is substantial of certain success.

While compass marine is a great source of info and dynamite site for how to....like Pascoe...not the only expert/professional/hands on guru out there.

I also know there's some REALLY SMART, talented guys with lot's of boating experience on this forum too... :thumb::thumb::thumb: ...so I hope never to insult the intelligence of them...

But I am not convinced that the regular twist locks are a huge issue as tens if not hundreds of thousands are used every day and the small number of fires started by them (and many probably really aren't ultimately the plugs fault) tell the tale as well as the issues that people experience with marine CBs and bad power posts.

Which just reminded me....in my experience I would say that 90% or better of the really bad plugs are always at the power post and not the boat. Smart Plug is only boatside for now...correct?

So yes...I would love to see a better product or design...but if my problem is at the other end of the cord...how/why switch until marinas do?
 
Circuit breakers are mechanical devices. That means they wear over time and do not necessarily perform as intended, especially when used as an on-off switch which many people do.
They also are not necessarily manufactured to design specifications. I know this for a fact as I worked for a short time supporting a factory that manufactures circuit breakers. I won't name the company but you all know them and I'm sure they are not alone.
So taking both the above into consideration it is not surprising to me that breakers do not always trip when they should.
 
Circuit breakers are mechanical devices. That means they wear over time and do not necessarily perform as intended, especially when used as an on-off switch which many people do.
They also are not necessarily manufactured to design specifications. I know this for a fact as I worked for a short time supporting a factory that manufactures circuit breakers. I won't name the company but you all know them and I'm sure they are not alone.
So taking both the above into consideration it is not surprising to me that breakers do not always trip when they should.

Nobody likes a voice of reason around here....:D
 
So, some folks do not really beleive me when I say that a breaker can be significantly overloaded and still not trip.


How many amps, over how much time will it take to burn up #10 wire, and the connectors?
Quite a lot, as it turns out. The ohms resistance/meter of AWG 10 gauge wire is .00328. Current squared times resistance equals watts of heat. 90 amps flowing through 10 gauge wire will generate about 26 watts, equal to the heat output of a refrigerator light, which would trip a 30 amp breaker in 30 seconds or so absent a fault to ground. I assume the damage we see in the picture isn't the result of 30 seconds exposure to a refrigerator light.

Run the same amount of current through a 40 gauge wire with resistance of 3.44 and you can generate about 28,000 watts of heat, which is why if I were to explain what happened here, I would ask the manufacturer what the purpose of the "trip thermostat" they refer to is, since it doesn't appear to do what they say it will do, i.e. provide "Overload Protection - internal thermostat cuts power at the first sign of overheating." Having seen it before I would look to whatever circuitry is involved in the "trip thermostat" since like many electronic components, it ain't using 10 gauge wire.

Not trying to pick on the manufacturer - just questioning the wisdom of placing circuitry that will melt down when exposed to an amp or so of current with a 30 amp breaker protecting it.
 
Had a plug ignite in my hand some years ago. I then hard wired the cord to the boat with proper connections and appropriate strain relief, never had another issue. Fewer connections, no wear from repeated connect/disconnect = Fewer potential problems, makes sense to me :)
 
Just had a email chat with Terry at SmartPlug, he is aware of both failures and here is his reply:

"This failure is due to a poor installation. The electrician or boat owner did not follow the instructions. I have provided you with the photos below of the other boat in the Anacortes area that had a connector failure. You can have the best product but if it is installed incorrectly they will fail.

Notice how there are no compression/bit marks on the yellow exterior sheathing of the cord. These photos document that the installer did not read the instructions to properly install our connector. The cord restraint jaws are designed to grip the yellow sheathing of the cord to eliminate pulling and strain on the wires that are installed in the connector. After prolonged use the pulling strain on the wires caused them to come loose which results in the failure as pictured in these photos. Please see the illustration below that is included with the installation instructions."

All I know is when I installed mine it was tough doing up the screws as to the pressure being put on the yellow jacket. No affiliation with Smartplug, just a happy customer.
The manufacturer is quite right that once the connection point is compromised, resistance can go up sufficiently to cause a melt down without drawing enough current to trip the breaker. That can be from water intrusion, or a loose connection. I guess I just question how much this particular product adds to safety when its installation method appears to be a bit sensitive to operator error, and it utilizes a feature that apparently doesn't work - the ability to shut off current when any heat is present.
 