A mystery I am hoping the forum can help solve.
The Victron Connect mppt 100/50 solar controller on board Bluechip keeps cutting the charge back to 0 amps during peak output times, after dropping to 0 then the amp rate raises again until battery voltage reaches just over 14 volts then the cycle starts again. Amp output when this happens is over 40 amps. It can cycle like this multiple times in a minute. On occasions the monitor shows a high voltage warning. The cycling significantly reduces the charging at peak sun time.
I have 2 x 345 watt sunpower panels feeding the controller which is hooked up to the house bank of 3 x 10 month old Ritar 260 amp agm batteries. The solar system was installed by a marine electrician in March this year.
The cycling occurs in both bulk and absorb stages and the only way I can prevent it happening is to limit the controller output to under 35 amps.
The normal load on the house bank is between 15/25 amps per hour on average running a freezer and 3 fridges plus water pumps/chargers etc.
I have had the controller replaced under warranty however the new one is doing exactly the same.
Any suggestions for me to investigate?
Settings
Just before it shuts down
After shutdown
The Victron Connect mppt 100/50 solar controller on board Bluechip keeps cutting the charge back to 0 amps during peak output times, after dropping to 0 then the amp rate raises again until battery voltage reaches just over 14 volts then the cycle starts again. Amp output when this happens is over 40 amps. It can cycle like this multiple times in a minute. On occasions the monitor shows a high voltage warning. The cycling significantly reduces the charging at peak sun time.
I have 2 x 345 watt sunpower panels feeding the controller which is hooked up to the house bank of 3 x 10 month old Ritar 260 amp agm batteries. The solar system was installed by a marine electrician in March this year.
The cycling occurs in both bulk and absorb stages and the only way I can prevent it happening is to limit the controller output to under 35 amps.
The normal load on the house bank is between 15/25 amps per hour on average running a freezer and 3 fridges plus water pumps/chargers etc.
I have had the controller replaced under warranty however the new one is doing exactly the same.
Any suggestions for me to investigate?