Hi,
The 100/50 VictronConnect mppt controller is located in the lazerette, ambient is 30 c and controller temperature is 48 c, rated for full power to 60c so I think that's not the issue. Battery external case temperature is 25/26 c.
In terms of battery bank the house batteries are 760 amps of agm, float 13.8 and absorb 14.4. House load is a constant 15 to 30 amps for fridges, freezer, pumps etc.
Once house bank reaches 13.7 vsr's connect in start, genset, windlass and thruster batteries which is over 1400 amps so difficult to overcharge them.
I have tried running the batteries down but still get the cycling at a rate of once every 6 seconds once panel watts exceed 500/550.
On the genset or engines batteries will take 120 amps easily at bulk charge rate.
I know it's a new unit as I fitted the replacement!!
Cables are doubled (?) and have sufficient capacity to carry 100 amps according to the installer.
I believe the controller can't cope with the panel output in spite of the panels being within the 100 volt/50 amp rating.
The problem is back with the supplier and installer at the moment who are both saying it should have the capacity and even if it didn't it tops out the charge rate not reduces it to zero!! We will see but unless they find another solution I will be wanting a higher rated controller to try!!
What a mystery! Thank you for taking the time to reply.