Victron Shunt settings. Help please.

The friendliest place on the web for anyone who enjoys boating.
If you have answers, please help by responding to the unanswered posts.

mvweebles

Guru
Joined
Mar 21, 2019
Messages
7,710
Location
United States
Vessel Name
Weebles
Vessel Make
1970 Willard 36 Trawler
Right now, I'm pulling drywall at our house and the only power we have is a simple 100w panel driving a 100ah LFP battery via a Victron 75/15 MPPT. I also installed a Victron Smartshunt. All this to run a small fridge and recharge my cordless tools which has been invaluable.

I cannot get the monitor to read properly.

First. It's bright sun here today. Gorgeous day to pull Sheetrock

#1. At 11:30 this morning, shunt showed showed system voltage of 12.83v and consumed AH of 60.6ah.
Screenshot_20241013_124057_Photos.jpg

#2. One hour later (12:41) voltage has increased to 12.97v so clearly it's receiving a charge from the MPPT, but the AH consumed continues to increase negative (as does the SoC).
Screenshot_20241013_124125_Photos.jpg

#3 for reference, here are my battery settings on the shunt.
Screenshot_20241013_123508.jpg

#4. And the settings on the MPPT
Screenshot_20241013_125442.jpg

Screenshot_20241013_125457.jpg


So the system is charging fine but the readings are not correct - AH consumed are not adjusted for solar charge from MPPT. What am I doing wrong?

Thanks in advance

Peter
 

Attachments

  • Screenshot_20241013_125457.jpg
    Screenshot_20241013_125457.jpg
    58.8 KB · Views: 1
first set mppt charger on lifepo4 not used defined.
second on 12,83v battery is on 5-10%

set charging 14,4
 
Is the ground for the MPPT going through the shunt? If anything is grounded directly to the battery and not through the shunt then it won't be measured.
 
First, I don't own any Victron gear.

From your displayed values, I would at least do these things to improve accuracy.

Set Peukert Exponent to 1.0 or whatever your battery manuf. says it is. 1.25 is a typical lead acid value.

Set Charge Efficiency to 98% or whatever the battery manuf. says.

If possible, set Auto Equalize to never, or get an understanding of what it is and set it correctly.

Then I think you need to get the battery to fully charged and manually set the current state of charge to 100%.

Read to find out what the actions mean for Sych SOC to 100% and Battery SOC on Reset and chose if you want to implement these actions.

Set all other parameters to whatever the battery manuf. recommends.

RTM.

Hope this helps.
 