On the Westerbeke 8BTD the stop switch releases the solenoid. Opposite to what you are thinking. It is a two stage solenoid with a Pull On and a Hold coil. When you turn it on it should Pull in and after it starts it should hold until you hit the stop switch. It should always be on while the generator is running. If the solenoid is bad or the linkage is corroded you can wire it in place in the pulled in position and it will allow fuel to flow.
You should also hear the fuel pump clicking when the switch is turned on. If not, the fuel pump may be bad. There are two models used in that unit, round and square, not interchangeable.
If the above two conditions are not present it will never start.
If your controls are at the genny it is a one man job but if you are at a remote switch you may need a second person at the unit listening for the fuel pump and watching the solenoid activate when the switch is turned to On and start.
You should also hear the fuel pump clicking when the switch is turned on. If not, the fuel pump may be bad. There are two models used in that unit, round and square, not interchangeable.
If the above two conditions are not present it will never start.
If your controls are at the genny it is a one man job but if you are at a remote switch you may need a second person at the unit listening for the fuel pump and watching the solenoid activate when the switch is turned to On and start.