I'll check him out for sure. ThanksI strongly suggest you watch some of the videos on Will Prowse's vlog, he is self taught and very good. He is into batteries, particularly lithiums and solar power. He reviews cheap versus expensive solar panels and comes up with some surprises. He also has recommendations for panels.
https://www.youtube.com/channel/UCoj6RxIAQq8kmJme-5dnN0Q
Thanks for the heads up about the controler.Renogy is a pretty good brand which came from obscurity 4-5 years ago and now has a wide range of DC electrical systems at very reasonable prices.
The package is ok, but you can save quite a bit of money by buying individual components (price them on Amazon and see) as well as upgrade to a better MPPT controller- Renogy or Victron (one of the best). The money you will save on the individual components should pay for the upgraded controller.
David
You're right.Consider cancelling the battery sensor and order a real battery monitor, either the Victron BMV 700 or the Renogy Battery Monitor. Either are shunt based meters that display real amperage used either intantaneous or amp hours over time. Amp hour usage is very important at managing your batteries. They also display voltage.
David
I did an Amazon search for balmar sg200 soc. Nothing came up. What is it?I am in the process of replacing my house bank and am going with a Balmar Sg200 SOC meter. It has some really good reviews so time will tell.
Question about the app. Yours reads 428 wattsI installed a Victron MPPT controller with the Victron Direct Dongle and have been very satisfied. Here is what the display looks like (Iphone)
Question about the app. Yours reads 428 watts
60 volts
7 amps
Is that what you're using or what the panel is making? Mine shows numbers but my inverter monitor shows I'm discharging the same 7 amps as I was before the install.
Btw how many panels?
I am surprised that it is receiving 61 volts and 7 amps from the three panels. That is about 20 volts from each panel wired in series and is much higher than the Vmp that the controller is trying to maintain (typically 16-17 V) and very close the the maximum Voc value of 21 V. At 20V I would have expected the current to be much lower than 7 amps.
But I can't argue with success although I don't like 3 or more panels wired in series. That is too high of a voltage for most DC wiring and components. For example, most DC surface mount circuit breakers are limited to 48V.
David
I think I'm running correctly. I got 21 volts at each panel and 18 volts at the controller loss of 3 volts over 40 plus feet of cable sound okay to you guys?
I used 10 awg.
Series with 10 awg.Looking back you have two 100 watt panels wired in parallel, right? A 3 volt drop is awful. With 10 gauge wire 40' long with about 12 amps it can't be that high. It should be about 1 volt or 1/2 volt if you wired them in series.
David
The 6.3 amps is what's going into your battery bank at 13.24 volts from the Victron. That's the output side of the Victron after converting the input volts/amps to something your batteries can digest.
Swipe left to see history graphs, if you haven't done so already.