Senior Member
Had the salon air handler unit start overflowing two days ago. Blew the lines out but still leaking so yesterday I shop vacuumed them to back flush still leaking.
Today I replaced the complete line from salon to bilge, still leaking.
If I go to the bilge and draw on it ever so slightly water comes pouring out but doesn’t continue to run. It’s like I need to vent the line to get it to flow. The line is 1/2” id and has 4 ‘ of fall. I can run a cable all the way through with no obstruction.
Any thoughts?
Today I replaced the complete line from salon to bilge, still leaking.
If I go to the bilge and draw on it ever so slightly water comes pouring out but doesn’t continue to run. It’s like I need to vent the line to get it to flow. The line is 1/2” id and has 4 ‘ of fall. I can run a cable all the way through with no obstruction.
Any thoughts?