So I am adjusting the settings on my Victron MPPT solar charger.
I am using a bank of 4 L16 AGM 6v batteries. Each battery has 3 cells. Two sets of batteries are connected in series and those two sets are connected in parallel for a 12v system.
Here is the question, the batteries call for -4mV/cell temp compensation per C° above 27°C.
So, I am thinking that this would be -24mV for this battery bank. Being in series, each pair of 6v batteries has 6 cells. However the total bank has 12 cells.
So would the temp compensation be -24mV/C° or -48mV/C°?