We purchased a boat with an 8.0 Kw MDKD generator (240V). The generator had a low voltage issue when we purchased the boat. We reduced the price by what the Onan tech gave us as a repair estimate. Six Weeks later and over 100 hrs of troubleshooting and no solution. These are the readings and symptoms. I am hoping someone may have an idea out there in trawler world.
Thanks in advance
History: Problem is low output voltage. It is transformer regulated. Output
voltage is 94VAC, 62Hz with load and about 60VAC, 63Hz unloaded
Genset is configured for 120/240 output @ 60Hz
Unit has a new Broward Armature rewound stator and rotor. Also a new exciter stator and T21 regulation transformer P/N 315-0572.
Current status: Troubleshooting is complete. Fuel transfer pump has been
replaced. Exciter rotor has not been replaced.
Onan model: 8.0mdkd-3cr/1a
Onan spec: A
Fluke 179 digital voltmeter was used for all tests.
The following tests have been done with these results:
[A] AC Residual voltage: 8VAC
[C] CR21 and RV21: Diode check with a Fluke digital meter shows all four
diodes in bridge are good with forward resistance being .5VDC on diode check
and 0 VDC for reverse. RV21 shows infinite resistance in both directions.
[D] Flash the field: Flashed with 9 volt battery saw slight increase in
output voltage, flashed with two 9 volt batteries in series for 18VDC,
voltage increased to 126VAC.
[G] Rotating rectifiers: F1+ to CR1,CR2,CR3 Showed .5VDC forward and 0VDC in
reverse. F2- to CR4, CR5, CR6 showed .5VDC forward and 0VDC reverse.
[H] Exciter stator: 12.5 ohms between F1+ and F2-. over 1Mohm with megger to
ground.
[J] Exciter rotor: T1-T2= .7 OHMS, T2-T3= .7 OHMS, T1-T3= .7 OHMS. Over 1
Mohm to ground on megger test.
[k] Generator stator: T1-T2=.2 OHMS, T3-T4= .2 OHMS. Over 1 Mohm to ground
with megger.
[L] Generator rotor: F1+ - F2- = 3.1 OHMS. Over 1 Mohm to ground with
megger.
[M] Wiring harness: No opens or corroded connections noted.
[N] T21 regulating transformer: H1-H2= .2 OHMS, H3-H4= .2 OHMS, X1-X2=.2
OHMS, X1-X4=1.2 OHMS, X1-X3=1.2 OHMS. Megger shows open between primary and
secondary.
Thanks in advance
History: Problem is low output voltage. It is transformer regulated. Output
voltage is 94VAC, 62Hz with load and about 60VAC, 63Hz unloaded
Genset is configured for 120/240 output @ 60Hz
Unit has a new Broward Armature rewound stator and rotor. Also a new exciter stator and T21 regulation transformer P/N 315-0572.
Current status: Troubleshooting is complete. Fuel transfer pump has been
replaced. Exciter rotor has not been replaced.
Onan model: 8.0mdkd-3cr/1a
Onan spec: A
Fluke 179 digital voltmeter was used for all tests.
The following tests have been done with these results:
[A] AC Residual voltage: 8VAC
[C] CR21 and RV21: Diode check with a Fluke digital meter shows all four
diodes in bridge are good with forward resistance being .5VDC on diode check
and 0 VDC for reverse. RV21 shows infinite resistance in both directions.
[D] Flash the field: Flashed with 9 volt battery saw slight increase in
output voltage, flashed with two 9 volt batteries in series for 18VDC,
voltage increased to 126VAC.
[G] Rotating rectifiers: F1+ to CR1,CR2,CR3 Showed .5VDC forward and 0VDC in
reverse. F2- to CR4, CR5, CR6 showed .5VDC forward and 0VDC reverse.
[H] Exciter stator: 12.5 ohms between F1+ and F2-. over 1Mohm with megger to
ground.
[J] Exciter rotor: T1-T2= .7 OHMS, T2-T3= .7 OHMS, T1-T3= .7 OHMS. Over 1
Mohm to ground on megger test.
[k] Generator stator: T1-T2=.2 OHMS, T3-T4= .2 OHMS. Over 1 Mohm to ground
with megger.
[L] Generator rotor: F1+ - F2- = 3.1 OHMS. Over 1 Mohm to ground with
megger.
[M] Wiring harness: No opens or corroded connections noted.
[N] T21 regulating transformer: H1-H2= .2 OHMS, H3-H4= .2 OHMS, X1-X2=.2
OHMS, X1-X4=1.2 OHMS, X1-X3=1.2 OHMS. Megger shows open between primary and
secondary.