sorry,needed to check codebook on this one.According to the nec,not abyc,and I quote from 400-8 as to uses not permitted,Flexible cords are not to be used as a substitute for fixed wiring of a structure.Attaching it permanently to the boat creates a fixed wiring situation.There are also addendums as to protection,and supports needed.The cablemasters complies with these nec codes by creating a retractible system that is independently hooked up by the cablemaster,while also complying with the protection issued by reeling the wire up when not in use.In other words,the other end of the shore power cable from the glennmaster is attached to the glennmaster,by approved methods,then the cablemaster connects to the power source.The shore power cable does not go directly to the boat buss.Hope that helps.
I have a question (in an attempt to get us back on track)...
Would it make sense to have both connectors on the boat side? You know, in case you DO drop one overboard or something. I don't imagine it would be safe to just parallel the plugs because when one was energized, the pins of the other would be passing current, but I don't see it and an extremely difficult problem to solve. Have a smart plug as primary, but maintain the old Hubble connector.
But you know... As I sit here and type this, I suppose a pigtail from SmartPlug to twist would be safer, easier, and cheaper to do sould something horrible happen to your primary and you need to borrow or buy one in a rush.
Nevermind.
One would hope.Exactly Wes,thats why two means of disconnect would be required.You cant bi-feed a busbar from two separate power sources legally.Anyone who has a genny(boat or home)has a transfer switch,thus allowing only one power source at a time,while locking out the other.
...I urge everyone to look over the Compass Marine article & photos and make your own decision - for what ever reasons you like....
I referenced this article on the very first page of this thread (post #4).
Just pointing this out because I am feeling left out this late in the thread...
It is an interesting article though and yes, we have specified that our new boat be equipped with Smartplugs. I'm not worried about finding a replacement as I will simply have a spare aboard!
I'm not sure why Tomco doesn't supply the boat with a 50 amp cord. I do know that they split air conditioning from everything else and give it its own cord... Is a single 50 amp cord and receptical more expensive than a pair of 30's?
I will ask about all of this and report back!
Bruce
"Is a single 50 amp cord and receptical more expensive than a pair of 30's?"
A single 120V 50A power cord is history not likely to be found on a dock.
PIA to use but the 240V 50A setup is probably the best bet , even if the boat can only draw 30a per leg.
Two inlets without a switch to allow only one to be used at a time would create a situation where the pins of the inlet not in use would be "hot" and that's a dangerous situation indeed.
Corrosion is not the big enemy of copper inhibiting its ability to conduct electricity,oxidation is,which boeshield makes no claim on.Think your water mains at your house,they are copper,and corrosion was the big enemy,copper would never have been used for that purpose,in fact,there ability to resist corrosion was why copper was chosen.Im not saying that copper doesn't corrode,but that it has a high resistance properties.From the boeshield website,they claim to inhibit corrosion,displace water,and lubricate.No mention of oxidation.Sounds very close to the claims of wd-40 to me.It may be superior to wd 40,no argument here with some additional capabilities over wd-40.I just feel that there are better alternatives.IMHO.
I referenced this article on the very first page of this thread (post #4).
Just pointing this out because I am feeling left out this late in the
... I do know that they split air conditioning from everything else and give it its own cord...
Bruce
sorry,needed to check codebook on this one.According to the nec,not abyc,and I quote from 400-8 as to uses not permitted,Flexible cords are not to be used as a substitute for fixed wiring of a structure.Attaching it permanently to the boat creates a fixed wiring situation.
When using standards and codes it is essential that you lok at the Purpose and scope The NEC is produced by the NFPA in is scope it specifically states "(B) Not Covered. This Code does not cover the following: (1) Installations in ships, watercraft other than floating buildings, railway rolling stock, aircraft, or automotive vehicles other than mobile homes and recreational vehicles "
NFPA has a separate standard NFPA 303 for boatyards and marinas. I sat on this panel for a decade.
1.1 Scope. This standard applies to the construction and operation of marinas, boatyards, yacht clubs, boat condominiums, docking facilities associated with residential condominiums, multiple-docking facilities at multiple-family residences, and all associated piers, docks, and floats. 1.1.1 This standard also applies to support facilities and structures used for construction, repair, storage, hauling and launching, or fueling of vessels if fire on a pier would pose an immediate threat to these facilities, or if a fire at a referenced facility would pose an immediate threat to a docking facility. 1.1.2 This standard applies to marinas and facilities servicing small recreational and commercial craft, yachts, and other craft of not more than 300 gross tons. 1.1.3 This standard is not intended to apply to a private, noncommercial docking facility constructed or occupied for the use of the owners or residents of the associated single-family dwelling. 1.1.4 No requirement in this standard is to be construed as reducing applicable building, fire, and electrical codes.
Neither of these apply to recreational boats. ABYC and NFPA 302 standards apply to recreational boats.
Bruce...
I thought your ref to the Compass article was worth repeating given the # of posts.
If you have 2 -30A cords/inlets consider having a panel w a transfer sw to connect both sides to one cord. Our Mainship is set up this way and I can run anything I choose w only one cord attached... I just have to manage load to keep it at 20-25 A when using one cord.
Some lications especially when traveling I may only have access to one 30A outlet.
I can provide more info if necessary and you are interested.
glad you chimed in,as that was my request that someone more familiar with abyc than I am.thankssorry,needed to check codebook on this one.According to the nec,not abyc,and I quote from 400-8 as to uses not permitted,Flexible cords are not to be used as a substitute for fixed wiring of a structure.Attaching it permanently to the boat creates a fixed wiring situation.
When using standards and codes it is essential that you lok at the Purpose and scope The NEC is produced by the NFPA in is scope it specifically states "(B) Not Covered. This Code does not cover the following: (1) Installations in ships, watercraft other than floating buildings, railway rolling stock, aircraft, or automotive vehicles other than mobile homes and recreational vehicles "
NFPA has a separate standard NFPA 303 for boatyards and marinas. I sat on this panel for a decade.
1.1 Scope. This standard applies to the construction and operation of marinas, boatyards, yacht clubs, boat condominiums, docking facilities associated with residential condominiums, multiple-docking facilities at multiple-family residences, and all associated piers, docks, and floats. 1.1.1 This standard also applies to support facilities and structures used for construction, repair, storage, hauling and launching, or fueling of vessels if fire on a pier would pose an immediate threat to these facilities, or if a fire at a referenced facility would pose an immediate threat to a docking facility. 1.1.2 This standard applies to marinas and facilities servicing small recreational and commercial craft, yachts, and other craft of not more than 300 gross tons. 1.1.3 This standard is not intended to apply to a private, noncommercial docking facility constructed or occupied for the use of the owners or residents of the associated single-family dwelling. 1.1.4 No requirement in this standard is to be construed as reducing applicable building, fire, and electrical codes.
Neither of these apply to recreational boats. ABYC and NFPA 302 standards apply to recreational boats.
alI am not a chemist, but I am pretty sure that oxidation is the most common form of copper corrosion. It is by definition the product of copper corrosion. In the presence of sea water I believe copper develops and oxide coating. The color of the coating varies with the chemistry of the copper alloy, the water and the amount of sulfur and oxygen available in the process. Pure cuprous oxide is red. The green patina a that we see on copper and bronze is the result of sulfur in the air and water and as the copper corrodes it often turns black first as result of lead in the alloy. The black color on copper wire is not carbon, it is merely the corrosion of the copper alloy itself.
The water lines in your house carry fresh water. Copper lines carrying salt water do corrode and have to be replaced from time to time.
Bruce...
I thought your ref to the Compass article was worth repeating given the # of posts.
If you have 2 -30A cords/inlets consider having a panel w a transfer sw to connect both sides to one cord. Our Mainship is set up this way and I can run anything I choose w only one cord attached... I just have to manage load to keep it at 20-25 A when using one cord.
Some lications especially when traveling I may only have access to one 30A outlet.
I can provide more info if necessary and you are interested.
Seen this happen at a home,when the power system was restored,the transformer was being backfed,blew it right off the pole,when they bucked.Not popular with the neighbors as they were in a power outage situation again,and I believe the municipality,in conjunjunction with the power authority imposed a ten thousand dollar fine,for damages,and unlicensed work.Ouch!! I was contracted to do the correct job.Just about everything was fried.
Corrosion is not the big enemy of copper inhibiting its ability to conduct electricity,oxidation is,which boeshield makes no claim on.T
https://en.wikipedia.org/wiki/File:Copper_wire_comparison.JPG
Unoxidized copper wire (left) and oxidized copper wire (right).
...copper will suffer from oxidation,regardless of the environment,as it attempts to return to its natural state.The marine environment just complicates it. Thanks
not sure what you mean I referred to. went back thru my posts,no mention of ac anywhere - alternating current,air conditioning?Where exactly is the copper you refer to in the boat AC system???
I did the same when designing my electrical system...
Other thing, turn off your boat main breaker on the unused 30 amp side, so the unused 30 amp connector socket is not energized, otherwise it will be live. I use a GE breakered weatherproof box, I put in 2 30 amp dual pole breakers, and I can lock the door shut.
The box never gets wet. It is about 6 feet from the shore power sockets.