It would be helpful, then, to understand why most large scale systems have earthed neutrals and also why using ground referenced supplies introduce a new risk for shock potential.
This added risk does not exist when both sides on the line are floating off ground.
Further, the potential benefits of isolation transformers are negated when one earths one of the output lines.
What i call “large scale” installs require earth tied feeds to mitigate two kinds of faults. First, it provides a path for lightning currents. Second, it reduces the damage caused by primary to secondary faults in step down distribution transformers. Either of which would otherwise likely cause severe damage downstream.
Small scale installs don’t have those two threats, and so have no benefit from “one side grounded” designs. In fact, doing so increases human shock potential. GFCI ‘s do help though.
I am not going to dwell on AC distribution methods other than to briefly mention the perils of floating systems such as the three phase deltas commonly found in power distribution. Back it the days of yesteryears, linemen worked with bare hands on high voltage wiring. They could because the system was ‘floating.’
But things changed forcing linemen to use insulated gloves and tools because there could be no guarantee that a tree branch was not touching one of the so call floating wires allowing ground current to flow and exposing the lineman to dangerous voltages. Another comment on floating systems is they are affected by static voltages that can build quit high. Because distribution lines are long, the capacitance to ground can be large storing high amounts of energy. Stored static energy in joules is 1/2(C*V^2). Note the function of V squared. But enough of power distribution. It has been a long time since I was a young electrical circuit design engineer.
Now to inverter issues! Inverters make AC, pseudo or true sine waves and DO NOT HAVE FLOATING OUTPUTS! OK....maybe some weirdo can put together a circuit that will, not the case though for the inverters advertised for vehicle usage.
I have several utility outlets for general use that I want energized while on dock power or my inverter. But the grounded conductor MUST be isolated from the inverter. The grounded conductor and the grounding conductor are married together at either the dock’s power pedestal or at a load center used for the dock’s power. A grounded conductor imposes a SHORT CIRCUIT on the inverter’s output. The inverter output must be isolated from the dock’s ground otherwise, it will destroy the inverter. Sure, I could use an elaborate relay scheme to isolate the problem. I could also use the inverter as an isolated power source rather than dock power.
So how does this happen? Inverters use what is known as an H bridge which I will explain using my sketch. The load in the center of the H bridge while the top of the bridge is connected to an internally developed voltage about 171 VDC. The bottom of the bridge is connected to the boat’s ground that is connected of course the the batteries’ negative return. The inverter’s object is to ‘make’ 120VAC RMS @ 60Hz. The peak voltage in a sine wave is equal to the RMS voltage times the square root of 2, close to 170V in this example. Because a voltage drop across the switches happens when the circuit operates, another volt or two most likely is needed from the DC supply to make the 120VRMS. The so called load shown also contains filters to make a sine wave. I describe an ‘on’ time for the switches which is the time period where the load is pulsed needed to make AC. The simplified circuit explanation is to help understand how the H bridge works.
The circuit requires two switches to close at the same time and then alternate with the opposite switches. Consider SW1 and SW4 closed. Current will flow from the 171VDC (top of bridge) through SW1, the load and SW4 back to then power source via the ground connection. This current is pulsed for 8.3 milliseconds equal to 1/2 of the 60Hz sine wave. The other half of the sine wave begins by opening SW1 & SW4 and closing SW3 and SW2 . The current now flows in the opposite direction through the load. Again, the conduction time is the same as current flowed in the other direction but pulsed
The points A & B represent the electrical connections one would find in a common wall outlet. But neither can be grounded! Consider placing a ground at point B. When SW3 closes it creates a SHORT CIRCUIT on the 171VDC power supply! The same will happen if a ground was placed at point A. SW1 would then short circuit the 171VDC supply
There are NO floating voltages in an H Bridge! Each side of the load is either close to 170V or ground potential. I want to be able to connect my inverter to wall outlets automatically after losing dock power. Why bother with complex circuitry when I can just use a transformer and be done with it. Can others do things differently? Of course. I got stung a couple of times operating my davit crane in wet weather powered from my inverter. An isolation transformer will prevent that. So that should provide a basic understanding of what goes on in an inverter.